I have been to a few Generator sizing sites and they all lead to huge generators.

 

My Home's Air Conditioner is a 47,000 BTU unit (3.91 Tons). According to the manufacturer, the running current is 24.7 AMPS @ 230 Volts. The maximum current listed is 40 AMPS. So I assume the most amount of power I need is between 9200-9600 watts to get it started and 5700-6000 to keep it running.

 

The Sizing charts I have found show my running power at 12,000 Watts and my starting power at over 22,000 Watts for a typical single phase, single stage, 4 ton unit.

 

What am I doing wrong??? I was always taught Voltage x Amps = Watts

 

One more question: Generators list a continuous and surge ability. In my case 15,000 Watt continuous and 22,000 Surge. If the generator has a 62 AMP circuit breaker how can it allow more than the continuous power without triping the breaker?

 

Thanks,

Vhato

Posted

Ohm's Law

 

Ohm's Law defines the relationships between (P) power, (E) voltage, (I) current, and ® resistance. One ohm is the resistance value through which one volt will maintain a current of one ampere.

 

( I ) Current is what flows on a wire or conductor like water flowing down a river. Current flows from points of high voltage to points of low voltage on the surface of a conductor. Current is measured in (A) amperes or amps.

 

( E ) Voltage is the difference in electrical potential between two points in a circuit. It's the push or pressure behind current flow through a circuit, and is measured in (V) volts.

 

( R ) Resistance determines how much current will flow through a component. Resistors are used to control voltage and current levels. A very high resistance allows a small amount of current to flow. A very low resistance allows a large amount of current to flow. Resistance is measured in ohms.

 

( P ) Power is the amount of current times the voltage level at a given point measured in wattage or watts.

 

ohmtable.gif

 

Hope this helps, I am a power Engineer but I am mostly DC and not AC.

Sorry

Posted
Ohm's Law

 

Ohm's Law defines the relationships between (P) power, (E) voltage, (I) current, and ® resistance. One ohm is the resistance value through which one volt will maintain a current of one ampere.

 

( I ) Current is what flows on a wire or conductor like water flowing down a river. Current flows from points of high voltage to points of low voltage on the surface of a conductor. Current is measured in (A) amperes or amps.

 

( E ) Voltage is the difference in electrical potential between two points in a circuit. It's the push or pressure behind current flow through a circuit, and is measured in (V) volts.

 

( R ) Resistance determines how much current will flow through a component. Resistors are used to control voltage and current levels. A very high resistance allows a small amount of current to flow. A very low resistance allows a large amount of current to flow. Resistance is measured in  ohms.

 

( P ) Power is the amount of current times the voltage level at a given point measured in wattage or watts.

 

ohmtable.gif

 

Hope this helps, I am a power Engineer but I am mostly DC and not AC.

Sorry

 

 

 

 

Wow ok!! That is cool stuff. I now understand the role impedance plays and see all equations. The problem is, when I try those equations I get 5.75 as the impedance, I always get 230 volts as voltage and 40 as amperage and 9200 as Watts. So the sizing charts are wrong?? Thanks for the pic!!

Posted

I have been doing more reading and now have more questions. Apparently A/C Compressors have a unit called LRA and this number determines how many AMPS are pulled to start up. My 4-ton unit needs 102 AMPS @ 230 volts (23,000 Watts) just to start, then falls to 18.3 RLA @ 230 volts (4200 Watts) of continuous power.

 

Now I am SUPER DUPER confused. I found a Generac Ultra Source Generator with a surge of 23,000 Watts and a continuous power of 15,000 Watts. It sounded like the perfect match for me, but the generator only has a 62.5 AMP Circuit breaker on the 230 Volt line. Thats just under 15,000 Watts of power.

 

So how on earth is the generator gonna put out a surge of 23,000 advertised watts when the breaker is gonna trip at 15,000 watts????????????????????????????????????????

Posted

Because the circuit breaker has some sort of inertia that prevents it from tripping during the surge.

Posted
Because the circuit breaker has some sort of inertia that prevents it from tripping during the surge.

 

 

 

 

 

Really? Sounds reasonable to me. Would you happen to know how much time can pass before tripping? Less than a second, 1-2 seconds, 3 or more??

 

Thanks!

Archived

This topic is now archived and is closed to further replies.

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Forum Statistics

    250.4k
    Total Topics
    2.7m
    Total Posts
  • Member Statistics

    342,822
    Total Members
    8,960
    Most Online
    ShipOfTheseus
    Newest Member
    ShipOfTheseus
    Joined
  • Who's Online   1 Member, 0 Anonymous, 675 Guests (See full list)

×
×
  • Create New...