The cord size will be determined by the amp draw. Long runs go next size up. If you are going to use all of the 9000 watts at 120 volts = 75 amps. Take the total watts you will be using and divide by 120 volts = amps. Don't forget motor start demand like on your fridge and freezer.

Amperage Capacities for Standard Non-Metallic (NM) Cable
16-gauge wire 13 amps
14-gauge wire 15 amps
12-gauge wire 20 amps
10-gauge wire 30 amps
8-gauge wire 40 amps
6-gauge wire 55 amps
4-gauge wire 70 amps
3-gauge wire 85 amps
2-gauge wire 95 amps

 

WIRE SIZING CHARTS

Maximum Ampacities for Wire


The table below shows allowable ampacities of conductors (wires) in conduit, raceway, cable or directly buried, in an ambient  temperature of 30°C (86°F). National Electrical Code (NEC) allows rounding up cable ampacity to next size standard fuse or breaker.

For ambient temperatures above 30°C (86°F), multiply the allowable ampacities shown at right by the correction factor listed under the insulation temperature rating below.

insolation2_large.png?v=1532642278

Insolation3_large.png?v=1532642335

 

 

 

Posted
20 minutes ago, diyer2 said:

The cord size will be determined by the amp draw. Long runs go next size up. If you are going to use all of the 9000 watts at 120 volts = 75 amps. Take the total watts you will be using and divide by 120 volts = amps. Don't forget motor start demand like on your fridge and freezer.

Amperage Capacities for Standard Non-Metallic (NM) Cable
16-gauge wire 13 amps
14-gauge wire 15 amps
12-gauge wire 20 amps
10-gauge wire 30 amps
8-gauge wire 40 amps
6-gauge wire 55 amps
4-gauge wire 70 amps
3-gauge wire 85 amps
2-gauge wire 95 amps

 

WIRE SIZING CHARTS

Maximum Ampacities for Wire


The table below shows allowable ampacities of conductors (wires) in conduit, raceway, cable or directly buried, in an ambient  temperature of 30°C (86°F). National Electrical Code (NEC) allows rounding up cable ampacity to next size standard fuse or breaker.

For ambient temperatures above 30°C (86°F), multiply the allowable ampacities shown at right by the correction factor listed under the insulation temperature rating below.

insolation2_large.png?v=1532642278

Insolation3_large.png?v=1532642335

 

 

 

The highest outlet on the inverter generator is a 4 prong twist lock 120/240 30 amp. It’s going to a interlocking plug to be installed by the breaker. I’m hoping to put the generator in my detached garage about 30ft from the house. I’m going to modify the exhaust to the outside. This is so during tropical weather I can service the generator during a storm. A  50 ft cord will be perfect. I’m hoping the breaker Is wired so I can turn on and off the ones I want to use. That will be my request anyway. My priorities are refrigerator, chest freezer and a 5000 window unit. My generator is a 8750 predator with 7000 watt running. I stay away from electricity. I leave it to the pros. Also I planning for my older age. The generator will be in a semi permanent location. I don’t want to pull around 165LBs. 

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Latest Articles

  • Posts

    • https://precisionlubrication.com/articles/oil-filter-efficiency/     For them it is a problem of $$$$ and compliance. To cover both they have to lie from the heart.    Government wants low waste oil numbers so the bar needs to be very low on contamination to met that requirement.  Consumer wants cheap maintenance (perceived cost). Again requiring a low bar.  OEM wants high margins at a cost effective warranty rate and lots of repeat customers. More low bar.  Filter manufacture wants the same thing the OEM wants. See the pattern?   Consumers are fickle and also want perfection requiring a HIGH bar. Inconsistent with all of the above. Consumers can be, when the put their minds to it, inquisitive, love winning arguments which requires some useful information to be available to support them. And this is where it gets sticky and the lies begin.    Information needs a solid well grounded point of reference if we are to compare in a useful way. There is a standard for this.  ISO 4548-12. This standard sets the particle size at a specific Beta ratio and darn few are faithful to its intent.    If they don't state the test method they change the particle size or the Beta ratio to hit a perceived favorable standard. They obscure the information in a way as to prevent direct comparisons leaving the consumer with one method. UOA's with an ISO 4406 test result. Pricey and not allot of labs willing to do the work. Lobby work happens everywhere, not just at the seat of government.       
    • IF,IF,IF. If they cared about quality instead of profit and this applies to any company, what a concept. 
    • Good Morning Gents..hope everyone is enjoying a beautiful saturday morning. I have a 2001 GMC Sierra that I bought used in 2018. I am the 2nd owner and its a beautiful truck. Ive put about 60,000 miles on it and recently the front end has felt funny. Kind of loose when hitting bumps adn sometimes I actually feel a "bang" in the steering wheel. I took it to a local guy who said that everything was tight and he tightened the steering box. It didnt feel much better, so I had him replace the front shocks, which had noto been done since I bought it. It had the check enging light on so I took it into a local garage to fix that and check out the suspension. Everything is original and the rubber bushings that I can see look bad. They said everything was tight and there wasnt any play in the front end. Im concerned about the banging feeling in the wheel. Ive been driving this truck for 8 years, so I know how it usually feels and this is something new. Its a second vehicle, so I dont drive it all the time, but Im trying to use it more often. I live out in the country and some of the  roads are kind of rough and I alive on gravel roads. Anyone deal with anything like this before? 
    • Yes of course. There’s no experience in the Trump organization in hiring contractors. it’s not like they’re experienced in that field.😆
    • Well, 2 no-bid contracts to donors didn't seem to result in a good job...
  • GM-Trucks.com Clubs

  • Popular Contributors

×
×
  • Create New...